what are the recommended input power cords? 2 prong or 3?
Title: Re: power cords
Post by: memphislights on January 13, 2009,
I believe that the recommended cord for the outputs is 2 prong since there is no ground strap.

I think that input would most likely be a 3 prong due to the recommended wire gauge to handle the 15A max input current.  I am assuming that most people will use an old PC power cable for this.  I think that you just do not connect the green ground wire to anything, so you either heatshrink the end or cut it flush.

Others probably know better though.


Now that I am thinking about it, would there be any negative effects, other than cost to adding a grounding post for all of the power cords? 
Title: Re: power cords
Post by: RJ on January 13, 2009,
I use three prong as said and cut off and shrink wrap the safety ground.  I never felt the extra ground was needed as the Lights themselfs do not have the ground plug.

RJ
Title: Re: power cords
Post by: Greg on January 13, 2009,
memphislights,

PC power cords aren't anywhere close to heavy enough in my opinion.  Most are 18 gauge some are 16.  14 gauge is probably the minimum you should consider for 15 amps input current with occasional peak excursions toward 20 amps.  I used 12 gauge (which is good for 20 amps continuous) on the LEs I built this past year.

Greg
Title: Re: power cords
Post by: memphislights on January 14, 2009,
Isn't the LE capable of dual AC inputs?  The 30A LOR systems are capable of dual power inputs and do use 14AWG for the input power cords and 18AWG for the outputs.  From what I have been reading, 14AWG is what is rated for 15A, but there is a caveat.  That rating is at 50C.  At lower temperatures, the safe current carrying capacity should be greater than at the rated "room temp".

On the other hand, almost everything that my friend is running is LED with the exception of a few incandescent items.

So at .03A per 50-60 ct LED string, and assuming a max working load current of 3A on each of the 6A triacs, that is around 100 strings per channel, and that is probably unlikely.  AT .3A per 100 ct incandescent, that is still 10 strings per channel, and I think that is probably unlikely as well.

So, assuming total amps at 30A for the unit, that would average out to around 2A per channel constant (60-70 LED strings or 5 incandescent strings per channel), but they probably won't be on constantly for long perionds of time.  You are only looking at a surge of 30A for probably less than a second, and that should trip your GFCI anyway.

I have plenty of the 18AWG to 14AWG PC power cords from PCS, servers, an monitors.  With ambient temps around 50F or lower during show times, this is only around 9C.  This should allow some additional overhead as far as conductor overheating.  This does not take into account any of the overhead that is built into the cable specs to begin with. 

All I am saying is that there is a perfect paper recommendation, but also a practical, safe, and less expensive  option as well.
I may still be wrong, but I will probably argue until my extension cord catches fire.


Oh, and if I am wrong about the dual AC input, then ignore what I just typed  ;D
Title: Re: power cords
Post by: Greg on January 15, 2009,
Yes the LEs are dual feed as designed, but I should think the majority of folks will use the LEs with the triac banks bridged as I did this past Christmas.

The most I pushed through any one of my LEs at any given time was about 25 amps for durations less than 30 seconds and a steady draw of just over 18 amps for several minutes at one point. The GFCIs I use are rated for 20 amps and are on dedicated 20 amp circuits with HACR type breakers.  I had no problems with GFCIs or breakers tripping.

At lower temps and more transient loading lighter wire may not be a problem for you.

If I hadn't had the heavier cords on hand, I might of used lighter wire and balanced up the loads more carefully across the controllers since 3 of them never exceeded an all on current of 6 amps for all 16 channels combined. :)
Title: Re: power cords
Post by: memphislights on January 15, 2009,
It really does matter how much you want to run through the system.

Just a side note, the LE manual says to jumper with spt-2 16AWG (10A) to run with a single AC input.  Doesn't really matter in my case, but I thought it was interesting.

I am just cheap, and will use as much of the free stuff that I have one hand.

2x 18AWG, 2x 16AWG, or 1x 14AWG, should work fine unless you get too ambitious.
Title: Re: power cords
Post by: ElectricCraft1 on January 15, 2009,
Just from the electrical standpoint; the National Electric Code states that 15 amp is #14 wire, 20 amp is #12 wire, and anything over 20 amp to 30 amp is #10 wire.  Now, there are exceptions as to wire type, and can therefore change these ratings, but this is the electrical code requirements for sizing of wire.  If there are any questions, just let me know.  I check post every couple of days.
Title: Re: power cords
Post by: ElectricCraft1 on January 16, 2009,
I suggest using low voltage landscape wire.  It is rated for use outdoors, comes in the appropriate sizes, and is cheap.  Install your own 2 wire cord caps and you're done.
Title: Re: power cords
Post by: ThaiWay on January 16, 2009,
^huh?

John
Title: Re: power cords
Post by: memphislights on January 16, 2009,
I think that he is talking about using the SPT-1 or SPT-2 to make your output cords.
Title: Re: power cords
Post by: ElectricCraft1 on January 17, 2009,
Yes, your output cords can be low voltage landscape wire.  It is similar to lamp cord, but is rated for use outdoors and comes in the #12 size.  Landscape wire is available through many sources including Home Depot and Lowes.  Check www.electricsuppliesonline.com/12lowvocawil.html as well.  The cord cap is the female plug end that you can pick up at any hardware store for a couple of bucks.
Title: Re: power cords
Post by: RJ on January 17, 2009,
Quote
Yes, your output cords can be low voltage landscape wire.  It is similar to lamp cord, but is rated for use outdoors and comes in the #12 size.  Landscape wire is available through many sources including Home Depot and Lowes.  Check www.electricsuppliesonline.com/12lowvocawil.html as well.  The cord cap is the female plug end that you can pick up at any hardware store for a couple of bucks.

I don't think we should be using wire rated at 12 volts to carry 120/240 volts. It is about the insulation as much as the size of the cable. If the wire is rated at 12 volts and not 120/240 the insulation is most likely not rated for the increased voltages.

The SPT wire that is rated for the highere voltages and can be bought from people Creative Displays can be bought cheaper so there really is no benifit to using the 12 volt cable that I can see.

Lets be safe and use the correct stuff.

Quote
Just a side note, the LE manual says to jumper with spt-2 16AWG (10A) to run with a single AC input.  Doesn't really matter in my case, but I thought it was interesting.

There are a few reasons this is fine on the LE.

first the jumper carries the load of 1/2 the board not the full load. So unless you overload or run the board way out of balance then you should be under 10 amps.

Second if you look at the Handbook of Electronic Tables and Formulas for American Wire Gauge. You will see that wire is rated under two uses.

1 - Transmission of power ( the normal use we have and what we quote all the time)
2 - Chassis wiring ( inside a case and a few inches at most, not bundled with other wires but open to air. Like in this use.)

http://www.powerstream.com/Wire_Size.htm

If you look up 16 awg you will see that for this use the wire is rated at 22 amps which is more than the whole LE is rated at with one feed. This should keep us well within ratings.

Hope this clears up some stuff.

RJ
Title: Re: power cords
Post by: ElectricCraft1 on January 17, 2009,
Yes, insulation is just as important as conductor size.  I am not going to argue, especially with the site administrator.  These units are qualified as a temporary installation therefore fall under a different section in the National Electric Code.  My only concern is that the insulation of the SPT is not rated for outdoor use.  But, since these units are not listed, and are to be used only for personal hobby, there is probably no need to comply with these codes.  (I am not being sarcastic)  RJ,  you do a great job, keep it up.
Title: Re: power cords
Post by: memphislights on January 17, 2009,
After looking throught the PC power cords that I had lying around, I realized that all I had were 18AWG cords.  After cutting one open, I have to agree that they are not as suitable as I thought.

Ok, I am thinking about going 14AWG and dual supplying the LE.  I am going by suggestion and the fact that the LOR system uses 2x 14AWG inputs.

I haven't seen much as far as cheap 14AWG power cords.  I was thinking about cutting up a 14AWG extension cord and using the following male plug.

https://www.hardwareworld.com/Rubber-Handle-Cap-pPFKKWQ.aspx (https://www.hardwareworld.com/Rubber-Handle-Cap-pPFKKWQ.aspx)
http://www.hardwareandtools.com/invt/4169207 (http://www.hardwareandtools.com/invt/4169207)
http://www.acehardwaresuperstore.com/cooper-wiring-round-plug-15-amp-125-volt-p-17430.html (http://www.acehardwaresuperstore.com/cooper-wiring-round-plug-15-amp-125-volt-p-17430.html)

I figured that I would silicone around the wire and the cap.  I figure that around $1-2 per input cord isn't that bad.

Anyone have any other alternatives?

Title: Re: power cords
Post by: RJ on January 18, 2009,
Why do you need any ends?  If you do like me and go buy a cheap short ext cord. maybe 3' or 6' at the most.  Cut the female end off and cut the green wire off shorter than the other two and shrink wrap it where it can not touch anything. Then hook the wires up to the controller, The male end is already on the cord and weather tight.

RJ
Title: Re: power cords
Post by: memphislights on January 18, 2009,
Most of the cheap extension cords are 6' 16/2 at about $1.  I haven't seen cheap cords in 14AWG in the $1-2 range.
Title: Re: power cords
Post by: RJ on January 18, 2009,
OH!,

  Ok well you want find them for $1 - $2 they will cost a few bucks but if you find a cheaper way them I understand.

Like for the output cords instead of buying lots of premolded cheap ext cords this year I am just getting 1000 ft of SPT with the UV inhibitor and using the Vampire taps as it make a smaller setup with only one open plug hole and that gets filled when I plug the lights in.

It works out about the same unless someone picks up another HD 3 pack for $1.24 deal! LOL

Let me know what you come up with I am looking for a supplier for the power input cords that are cheap.

RJ
Title: Re: power cords
Post by: memphislights on January 18, 2009,
I went to HD, and they had plenty of the 3pk "holiday" cords, but they weren't on sale.  I looked into using the SPT and female plugs for the outputs like you are planning.

I found the 1000ft SPT-1 for $130 and the female plugs for .65 to .55 in quantity plus about $23 in shipping.  Did you find any better prices?

I guess I have another question now.  Do most people use a dual AC input or a single?  I am used to using the dual inputs on the LOR for 30A max, but with more channels controlling individual effects, unless you are stringing several together, the current draw should be less than 1A per channel (mostly LED's).  If that assumption is correct, then I should be able to get by with a single 14AWG input cord.  I could always dual cord if I expect the LE to have to drive more incandescents or multiples of something, right?

This leads me to the triacs on the LE.  They are rated at 6A.  I think that from the stuff that I read, if you are running at less than 1/2 of the rated amps, it should run relatively cool without a heatsink.  How is it in the LE in actual practice?

Slightly off of the subject for the last question, but better than opening up another post just for that.

 
Title: Re: power cords
Post by: RJ on January 18, 2009,
1 Amp a channel is fine with no heatsink be the coops come with it and it looks nice!  The rating has some effect on the ability to use it without a heat sink but ver little it is not double the rating and double the load as you are saying.  If you want more than 1 amp on a TO220 case since it can only dissipate so much heat in the area avaliable you need to attach it to something with a good path for the heat to move fast into it. A heatsink with a little heat compound is ideal.

No it will not self destruct at 2 amps as a few will jump in hear to say but it is a good idea to keep them cool.

As far as the cords As long as your cords will handle the max current you are going to use them for then you are fine. I used 3 expresses on my mega tree this year. One string of LED per channel. I used 2 cheap ext cords 16GA I think on it. They were not even close to a limit.
Yes I did find it cheaper. If you order before the end of the month on the pre sale form creative displays they have it for 1000' for $85 with the UV inhibitor in it. And the ends are like .40 I think it is.

RJ
Title: Re: power cords
Post by: wbuehler on January 18, 2009,
You can get a really good deal on SPT3 1000' from Paul over at CDI
Here is a link from the DIYC forum to his LED group buy thread which also has the wire and vampire plugs on the price sheet.

http://www.doityourselfchristmas.com/forums/showthread.php?t=5878

Title: Re: power cords
Post by: gjbankos on February 24, 2009,
So I'm not going to be building my own power cords.  That being said, it looks like 14 or 12 guage into my LE and cheap indoor power cords out of the LE is going to be fine?  I'm running LEDs with my LE, so my output needs won't be large at all.  Thank you in advance.
Title: Re: power cords
Post by: REM on February 24, 2009,
You are not allowed to view links. Register or Login
So I'm not going to be building my own power cords.  That being said, it looks like 14 or 12 guage into my LE and cheap indoor power cords out of the LE is going to be fine?  I'm running LEDs with my LE, so my output needs won't be large at all.  Thank you in advance.

Sounds like a winner to me!
Title: Re: power cords
Post by: magic8192 on February 25, 2009,
I might just buy the cords that solidmodeler found for .78 cents each in quantities of  100+

http://www.iofast.com/product_info.php/cPath/49_823/products_id/3919
Title: Re: power cords
Post by: brandonj on February 25, 2009,
You are not allowed to view links. Register or Login
I might just buy the cords that solidmodeler found for .78 cents each in quantities of  100+

http://www.iofast.com/product_info.php/cPath/49_823/products_id/3919


That is what i am doing.  I just wish they had a 6 foot version.  But i think it will make for a nice finishing tough on the express!
Title: Re: power cords
Post by: REM on February 25, 2009,
Spent some time at Lowes tonight trying to decide what to do about input power cords.  Ideally I'd like to have 2 20A-capable inputs.  The problem is that 20A plugs are all NEMA 5-20 "one-sideways-prong".  Extension cords with 12g and NEMA 5-20's are harder to find and expensive.  Now, you can buy a small quantity of 12-3 "service cord" for a buck and change a foot and add on the plugs but you still have the prong issue.  If you make your own 12g extensions to feed them with the full 20 amps then you're good.  If not, I guess you could still use an adapter and at least have the future capability - but even those aren't cheap at all.

Frankly I'm leaning toward just 15A per side and using something like this: http://www.iofast.com/product_info.php/cPath/49_777/products_id/3913 .  At 2 bucks and change you can't hardly beat that.  Heck, it's even SPT-3.

Guess I'll go ahead and get the .78 cent output cords from them too.  Maybe I should apply for some of that stimulus money ;)