calling all electricians
« on: November 02, 2011, »
I ran into a problem at work last night day shift look at me like I was smoke dope. I have a 480 step down transformer on the infeedI have 480 across the legs both 277 to ground the secondary I have 2 115 taps and 1 230  volt tap I have trouble with the 230 across the legs I have 230 one leg to ground is 200 the other is 50. I say replace they say can't be that.

mods feel free to delete

can any point me to a good forum non christmas lights to post these questions

Offline steve_hirst

  • Full Member
  • ***
  • Posts: 63
Re: calling all electricians
« Reply #1 on: November 02, 2011, »
First I would say to backtrace your ground and make sure that its a good ground. I had an issue once at a jobsite that was much like this one and it turned out that the transformer didn't have a good ground and that gave it alot of flex in the output voltage. If I remember right I had a hot on the lower leg that was shorted to ground and that was becoming the transformers ground refernce. this making the breaker not trip either. once I found the bad ground and fixed it, the breaker tripped and I found the short.

Offline n1ist

  • Coop Manager
  • Sr. Member
  • *
  • Posts: 760
  • 02148
Re: calling all electricians
« Reply #2 on: November 02, 2011, »
I agree with Steve; sounds like an open or high resistance ground on the secondary side.