Hardware => Lynx Aether => Topic started by: chrisatpsu on November 25, 2012,
-
I have two Aether II's connected to the same power supply. i have a short run on spt1 wire between the power supply terminals to the first aether II
I want to have a piece of spt1 wire also connected to the screw terminals of the power supply and run it to the 2nd aether II.
about how do you think i can get away with for the run on cable on the second aether II.
-
STP1 has more to do with the insulation thickness than anything else. If you are only putting 1 Aether on it, I doubt that you are going to have any issue with it regardless of the length that you would probably use.
-
i was meaning more for the voltage drop
-
Voltage drop is based on current flow so as I said, one Aether will not pull enough current to cause enough of a voltage drop to effect it. Also remember that if you are using an outdoor lighting transformer, the unloaded output voltage is way above 12V anyway so with only 2 units hanging on it, you should be good to go.
-
I have one 20 feet away from the transformer